Page 1 of 1

Syncrowave 350 new to me and jumper questions

Posted: Sat Oct 27, 2018 11:54 am
by cabinover
Serial number JK669265

Picked this up from a brazing shop in NH yesterday. Came with a TIGer cooler, all leads, and a CK20 torch. When it was unhooked from the breaker box, it says 480V next to the jumpers. Found the schematic inside left cover and looked at it this morning. The way I see it they had it jumpered for 200V. Jumper on 1&2, and another on 5&6. Am I missing something?

Anyway, I need 230V to be able to use it in my shop. From what I see that means jumping pins 2&3, and 4&5 correct? Pins 1 and 6 are left unhooked to anything. Ready to hook up sometime this weekend but don't want to let any magic smoke out.

I saw this machine weld so I know it was working, just don't understand how they had the jumpers set up.

Thanks ahead of time.

Re: Syncrowave 350 new to me and jumper questions

Posted: Sun Oct 28, 2018 12:17 pm
by MinnesotaDave
The manual for that machine doesn't show the jumpers and refers the owner to the tag you found.

Post a pic of the tag and your question can be answered more easily.

Re: Syncrowave 350 new to me and jumper questions

Posted: Sun Oct 28, 2018 3:14 pm
by cabinover
This is how it was wired at the shop I bought it from.
1028181502_resized.jpg
1028181502_resized.jpg (25.99 KiB) Viewed 712 times
This is what is on the schematic inside the welder, the same as what is in the Owner's Manual.
1028181500_resized.jpg
1028181500_resized.jpg (48.28 KiB) Viewed 712 times
Suppose it's possible that they were using one leg of 3 phase for 200 VAC, and the machine was labeled from another owner previously that had 480VAC power?

Sorry, apparently my Android takes sideways pics, or the computer re-orients them for some reason. On my desktop they are upright.
Thanks

Re: Syncrowave 350 new to me and jumper questions

Posted: Sun Oct 28, 2018 5:48 pm
by Poland308
They were using 208 single phase. You will probably be fine if you run it off 208. 230 or 460 single phase are the other options. (You will need to move jumpers) . We run lots of single phase welders off of single phase, the only cautions are 1 if you do it off of a gfci breaker it will probably fault out. 2 you need to know if your 3 phase has a wild leg, and if so make sure your single phase unit isn’t on it.

Re: Syncrowave 350 new to me and jumper questions

Posted: Sun Oct 28, 2018 6:39 pm
by cabinover
Just measured my line voltage. I have 239VAC across a double breaker. From what I've read Miller is ok with 10%+/-. So...I need to move my jumpers by the looks.

Am I correct in seeing posts 2&3, and 4&5 jumpered for 230V?


Glad I don't have any Argon yet, I'd be so chomping at the bit to play with this machine. Stopped at Lowe's today and grabbed my 100A breaker along with some wire ends. Should be running Tuesday night with nothing getting in the way.

Thanks

Re: Syncrowave 350 new to me and jumper questions

Posted: Sun Oct 28, 2018 8:37 pm
by Poland308
Yes that’s what the diagram shows.

Re: Syncrowave 350 new to me and jumper questions

Posted: Mon Oct 29, 2018 6:16 am
by cabinover
Thank you sir, and your signature line pretty much sums me up as well.